Question 2025 of 344 · NICET Fire Alarm Systems Level II
What test equipment is typically used for annual functional testing of spot smoke detectors in place?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2025
- A: Listed aerosol or smoke applied with a test cup
Explanation
Smoke detectors are tested in place with smoke or a listed aerosol acceptable to the manufacturer, which checks that smoke enters the chamber and alarm is produced. Open flames and heat guns are not used on smoke detectors.
More questions: Maintenance
- 2026What is the correct way to functionally test a restorable heat detector?
- 2027A technician bypasses a zone for testing and forgets to restore it. What risk does this create?
- 2028The control unit shows a ground fault trouble. What is the most efficient first step to locate it?
- 2029A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?
- 2031A Class B IDC with a 4.7 kilohm EOL resistor reads infinite resistance at the panel terminals with field wiring removed. What does this indicate?