Question 3019 of 344 · NICET Fire Alarm Systems Level II

A NAC uses 14 AWG stranded copper (3.14 ohms per 1000 ft). The appliances draw 1.5 A in total and the farthest one is 300 ft from the panel. What is the voltage drop, treating the load at the end?

Exactly one answer is correct.

Show solution

Correct answer to question 3019

  • A: About 2.8 V

Explanation

Loop length = 2 x 300 = 600 ft, so R = 3.14 x 600 / 1000 = 1.884 ohms. Drop = 1.5 A x 1.884 ohms = 2.83 V. Starting at the 20.4 V battery end voltage, the last appliance sees about 17.6 V.