Question 3020 of 344 · NICET Fire Alarm Systems Level II
A designer starts at 20.4 V (battery end voltage) and needs at least 16.0 V at the last appliance. The NAC draws 2.0 A and uses 12 AWG solid (1.93 ohms per 1000 ft). What is the maximum one way length, with the load at the end?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3020
- C: About 570 ft
Explanation
Allowed drop = 20.4 - 16.0 = 4.4 V. Maximum loop resistance = 4.4 / 2.0 = 2.2 ohms. Loop length = 2.2 / 1.93 x 1000 = 1140 ft, so the one way length is 570 ft.