Under the IBC, when is a manual fire alarm system required in a Group B occupancy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3023
- B: Combined occupant load of 500 or more, or over 100 above or below exit discharge
Explanation
Group B requires a manual system where the combined occupant load of all floors is 500 or more, or where more than 100 persons are above or below the lowest level of exit discharge. Ambulatory care facilities have their own trigger.