Question 3023 of 344 · NICET Fire Alarm Systems Level II

Under the IBC, when is a manual fire alarm system required in a Group B occupancy?

Exactly one answer is correct.

Show solution

Correct answer to question 3023

  • B: Combined occupant load of 500 or more, or over 100 above or below exit discharge

Explanation

Group B requires a manual system where the combined occupant load of all floors is 500 or more, or where more than 100 persons are above or below the lowest level of exit discharge. Ambulatory care facilities have their own trigger.