Under the IBC, when is a manual fire alarm system required in a Group A occupancy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3021
- B: Occupant load of 300 or more
Explanation
Group A occupancies need a manual fire alarm system where the occupant load is 300 or more, or where more than 100 persons are above or below the lowest level of exit discharge. Sprinklered buildings may omit manual boxes under the listed exception.