Under the IBC, a Group E occupancy needs a manual fire alarm system at what occupant load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3024
- A: 50 or more
Explanation
Group E occupancies with an occupant load of 50 or more require a manual fire alarm system that activates the occupant notification system. Some exceptions apply to small sprinklered schools with specific conditions.