Under the IBC, which condition requires a manual fire alarm system in a Group R-2 apartment building?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3026
- D: Units 3 or more stories above exit discharge, or over 16 units
Explanation
R-2 needs a manual system where any dwelling or sleeping unit is 3 or more stories above the lowest level of exit discharge, more than one story below it, or where the building has more than 16 dwelling or sleeping units.