Question 3027 of 344 · NICET Fire Alarm Systems Level II
Under the IBC, what fire alarm features are required in a Group R-1 hotel?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3027
- A: Manual fire alarm and automatic smoke detection
Explanation
Group R-1 occupancies require a manual fire alarm system and an automatic smoke detection system in interior corridors and common areas, in addition to smoke alarms in sleeping units. Small buildings with exterior exits have exceptions.
More questions: Submittal Preparation and System Layout
- 3028Under the IBC, when is a manual fire alarm system required in a Group F occupancy?
- 3029Under the IBC, which fire alarm requirement applies to Group I occupancies?
- 3030Under the IBC, a building is fully sprinklered and the occupant notification activates on sprinkler waterflow. What does the common exception allow for Group B or M?
- 3031Under the IBC, what is the maximum area of one fire alarm zone?
- 3032A single floor of a building covers 60,000 sq ft. What is the minimum number of IBC fire alarm zones for that floor?
- 3033A three story office building has floors of 12,000 sq ft each. How many IBC fire alarm zones are needed at minimum?