Under the IBC, when is a manual fire alarm system required in a Group M occupancy?

Exactly one answer is correct.

Show solution

Correct answer to question 3025

  • B: Combined occupant load of 500 or more, or over 100 above or below exit discharge

Explanation

Group M requires a manual system where the combined occupant load is 500 or more, or more than 100 persons are above or below the lowest level of exit discharge. A sprinkler exception may apply when waterflow activates notification.