What happens to doors held open by fire alarm controlled magnetic door holders when building power fails?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1019
- C: The doors are released and close
Explanation
Door hold-open devices are designed fail-safe: loss of power releases the doors so they close and maintain the smoke barrier. Systems are often designed so door holders are not carried on standby batteries, which also extends battery life.