Question 1020 of 297 · NICET Fire Alarm Systems Level III
An access-controlled egress door is electrically locked. What must happen to it when the building fire alarm system activates?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1020
- D: It unlocks in the direction of egress and stays unlocked until reset
Explanation
NFPA 101 requires access-controlled egress doors to unlock in the direction of egress on activation of the fire alarm system and on loss of power to the lock. NFPA 72 covers the interface: release must occur and remain until the fire alarm system is reset.
More questions: Installation
- 1021The fire alarm control unit will be in a storage room that is not continuously occupied. What detection does NFPA 72 require at the control unit location?
- 1023What mounting height does NFPA 72 require for the operable part of a manual fire alarm box?
- 1024Where must manual fire alarm boxes be placed in relation to exits, when they are required?
- 1025A lobby has a group of entrance doors whose total width exceeds 40 ft. How should manual fire alarm boxes be located?
- 1026During acceptance testing of a valve supervisory switch on an OS&Y valve, when must the off-normal supervisory signal appear?
- 1027A waterflow switch is tested by flowing water through the inspector's test connection. What performance does NFPA 72 require?