The fire alarm control unit will be in a storage room that is not continuously occupied. What detection does NFPA 72 require at the control unit location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1021
- D: Smoke detection at the control unit, or heat detection where smoke detectors would be unsuitable
Explanation
Control equipment in an area that is not continuously occupied needs automatic smoke detection so a fire threatening the panel is detected before it can disable the system. Heat detection is allowed where ambient conditions would make smoke detectors unreliable.