Question 1067 of 297 · NICET Fire Alarm Systems Level III
To which UL standard must a fire alarm control unit be listed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1067
- B: UL 864
Explanation
UL 864 covers control units and accessories for fire alarm systems. UL 268 covers smoke detectors for fire alarm service, UL 1971 visible signaling devices for the hearing impaired, and UL 2075 gas and vapor detectors such as carbon monoxide detectors.
More questions: Installation
- 1068A submittal for duct smoke detectors lists only a UL 268 listing. Which listing should you ask for instead?
- 1069Where are the installation requirements for carbon monoxide detection in a commercial building located for current NFPA 72 projects?
- 1070Which NFPA standard covers integrated testing of fire protection and life safety systems that interact with each other?
- 1071Your crew must connect new devices to an existing system in an occupied hospital, which will take the system out of service for part of a shift. What should happen first?
- 1072Under NFPA 101, what must happen when a required fire alarm system is out of service for more than 4 hours in a 24-hour period?
- 1074A remote booster power supply is added to drive strobes on the third floor. What must the Level III make sure is documented and done?