A submittal for duct smoke detectors lists only a UL 268 listing. Which listing should you ask for instead?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1068
- D: UL 268A, the standard for detectors used in ducts
Explanation
Duct smoke detectors are tested to UL 268A, which addresses the air velocities and sampling arrangements found in HVAC ducts. They must also be listed for the air velocity range in the duct where they will be installed.