Where are the installation requirements for carbon monoxide detection in a commercial building located for current NFPA 72 projects?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1069
- B: In NFPA 72 itself, because the former NFPA 720 content was incorporated into it
Explanation
Starting with the 2022 edition cycle, the carbon monoxide detection requirements formerly in NFPA 720 were moved into NFPA 72 and NFPA 720 was withdrawn. Occupancy codes such as the IBC and IFC decide where CO detection is required.
More questions: Installation
- 1070Which NFPA standard covers integrated testing of fire protection and life safety systems that interact with each other?
- 1071Your crew must connect new devices to an existing system in an occupied hospital, which will take the system out of service for part of a shift. What should happen first?
- 1072Under NFPA 101, what must happen when a required fire alarm system is out of service for more than 4 hours in a 24-hour period?
- 1074A remote booster power supply is added to drive strobes on the third floor. What must the Level III make sure is documented and done?
- 1075A building has a central station monitoring contract. What must be posted at the protected premises to show compliance?
- 1076On an addressable system, why does the Level III insist that the remote annunciator be located where the AHJ approves, usually at the fire department entrance?