Which NFPA standard covers integrated testing of fire protection and life safety systems that interact with each other?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1070
- D: NFPA 4
Explanation
NFPA 4 covers integrated system testing, which verifies that interconnected systems such as fire alarm, sprinklers, smoke control, elevators, and door hardware work together as intended. NFPA 25 covers water-based system ITM, NFPA 90A air conditioning systems, and NFPA 110 emergency generators.