Your crew must connect new devices to an existing system in an occupied hospital, which will take the system out of service for part of a shift. What should happen first?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1071
- A: Plan the impairment, notify the owner, AHJ, and monitoring station, and set up approved interim measures
Explanation
A planned impairment needs advance notice to the owner, the AHJ as required, and the supervising station, plus interim measures such as a fire watch. In health care occupancies, NFPA 101 also requires an approved fire watch or evacuation when the system is out of service for more than 4 hours in 24.
More questions: Installation
- 1072Under NFPA 101, what must happen when a required fire alarm system is out of service for more than 4 hours in a 24-hour period?
- 1074A remote booster power supply is added to drive strobes on the third floor. What must the Level III make sure is documented and done?
- 1075A building has a central station monitoring contract. What must be posted at the protected premises to show compliance?
- 1076On an addressable system, why does the Level III insist that the remote annunciator be located where the AHJ approves, usually at the fire department entrance?
- 1077The HVAC contractor has not yet started the air handlers when the fire alarm acceptance test is scheduled. What should the Level III project lead do?
- 1078Before final inspection, the sprinkler contractor asks to monitor the fire pump. Which conditions are typically supervised at the fire alarm system for an electric fire pump?