Under NFPA 101, what must happen when a required fire alarm system is out of service for more than 4 hours in a 24-hour period?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1072
- C: The AHJ is notified and the building is evacuated or an approved fire watch is provided
Explanation
NFPA 101 sets the 4-hour trigger for required fire alarm systems out of service. At that point the AHJ must be notified, and either the building is evacuated or an approved fire watch is provided until the system is restored.
More questions: Installation
- 1074A remote booster power supply is added to drive strobes on the third floor. What must the Level III make sure is documented and done?
- 1075A building has a central station monitoring contract. What must be posted at the protected premises to show compliance?
- 1076On an addressable system, why does the Level III insist that the remote annunciator be located where the AHJ approves, usually at the fire department entrance?
- 1077The HVAC contractor has not yet started the air handlers when the fire alarm acceptance test is scheduled. What should the Level III project lead do?
- 1078Before final inspection, the sprinkler contractor asks to monitor the fire pump. Which conditions are typically supervised at the fire alarm system for an electric fire pump?
- 1079Which of the following is the best way to deal with a scope gap discovered mid-project, where the contract drawings show no detection in a new IT room that the code requires?