Question 1072 of 297 · NICET Fire Alarm Systems Level III

Under NFPA 101, what must happen when a required fire alarm system is out of service for more than 4 hours in a 24-hour period?

Exactly one answer is correct.

Show solution

Correct answer to question 1072

  • C: The AHJ is notified and the building is evacuated or an approved fire watch is provided

Explanation

NFPA 101 sets the 4-hour trigger for required fire alarm systems out of service. At that point the AHJ must be notified, and either the building is evacuated or an approved fire watch is provided until the system is restored.