Question 1074 of 297 · NICET Fire Alarm Systems Level III
A remote booster power supply is added to drive strobes on the third floor. What must the Level III make sure is documented and done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1074
- C: Its own battery calculation, a dedicated monitored power source, and its location on the record drawings
Explanation
A remote power supply is part of the fire alarm system power and must meet the same rules: dedicated branch circuit with identified disconnect, secondary power sized by its own calculation, and supervision. Its location and circuit information must be on the record drawings so service crews can find it.
More questions: Installation
- 1075A building has a central station monitoring contract. What must be posted at the protected premises to show compliance?
- 1076On an addressable system, why does the Level III insist that the remote annunciator be located where the AHJ approves, usually at the fire department entrance?
- 1077The HVAC contractor has not yet started the air handlers when the fire alarm acceptance test is scheduled. What should the Level III project lead do?
- 1078Before final inspection, the sprinkler contractor asks to monitor the fire pump. Which conditions are typically supervised at the fire alarm system for an electric fire pump?
- 1079Which of the following is the best way to deal with a scope gap discovered mid-project, where the contract drawings show no detection in a new IT room that the code requires?
- 1080Why should a Level III verify the listing of every substituted device before it is installed?