Question 1074 of 297 · NICET Fire Alarm Systems Level III

A remote booster power supply is added to drive strobes on the third floor. What must the Level III make sure is documented and done?

Exactly one answer is correct.

Show solution

Correct answer to question 1074

  • C: Its own battery calculation, a dedicated monitored power source, and its location on the record drawings

Explanation

A remote power supply is part of the fire alarm system power and must meet the same rules: dedicated branch circuit with identified disconnect, secondary power sized by its own calculation, and supervision. Its location and circuit information must be on the record drawings so service crews can find it.

Next to question ›