A building has a central station monitoring contract. What must be posted at the protected premises to show compliance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1075
- A: Documentation of central station service from the prime contractor, posted within 3 ft of the control unit
Explanation
Central station service must be indicated at the protected premises by documentation from the prime contractor, such as a certificate issued under a listing program. It is posted conspicuously within 3 ft of the control unit, so the AHJ can see that a listed central station provides all elements of the service.
More questions: Installation
- 1076On an addressable system, why does the Level III insist that the remote annunciator be located where the AHJ approves, usually at the fire department entrance?
- 1077The HVAC contractor has not yet started the air handlers when the fire alarm acceptance test is scheduled. What should the Level III project lead do?
- 1078Before final inspection, the sprinkler contractor asks to monitor the fire pump. Which conditions are typically supervised at the fire alarm system for an electric fire pump?
- 1079Which of the following is the best way to deal with a scope gap discovered mid-project, where the contract drawings show no detection in a new IT room that the code requires?
- 1080Why should a Level III verify the listing of every substituted device before it is installed?
- 1081During rough-in inspection on a new office building, you find several fire alarm junction boxes above a hard lid ceiling with no access panel. What is the main concern?