Question 1076 of 297 · NICET Fire Alarm Systems Level III
On an addressable system, why does the Level III insist that the remote annunciator be located where the AHJ approves, usually at the fire department entrance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1076
- B: Responders need to read alarm locations as they arrive, before going into the building
Explanation
Annunciation is for responders, so it must be readily accessible at a location approved by the AHJ, typically the main entrance or fire command center. Placing it elsewhere for convenience of the installer defeats its purpose.
More questions: Installation
- 1077The HVAC contractor has not yet started the air handlers when the fire alarm acceptance test is scheduled. What should the Level III project lead do?
- 1078Before final inspection, the sprinkler contractor asks to monitor the fire pump. Which conditions are typically supervised at the fire alarm system for an electric fire pump?
- 1079Which of the following is the best way to deal with a scope gap discovered mid-project, where the contract drawings show no detection in a new IT room that the code requires?
- 1080Why should a Level III verify the listing of every substituted device before it is installed?
- 1081During rough-in inspection on a new office building, you find several fire alarm junction boxes above a hard lid ceiling with no access panel. What is the main concern?
- 1082A fire alarm interface relay will release the hold-open power for corridor smoke doors. How should the release be wired so it is fail-safe?