Question 1077 of 297 · NICET Fire Alarm Systems Level III

The HVAC contractor has not yet started the air handlers when the fire alarm acceptance test is scheduled. What should the Level III project lead do?

Exactly one answer is correct.

Show solution

Correct answer to question 1077

  • C: Reschedule or coordinate so the fan shutdown and damper functions can be observed working

Explanation

Acceptance testing must prove that emergency control functions actually operate the controlled equipment. Testing only the relay contact does not show that the fan stops or the damper closes, so the test must be coordinated with the trades that control the equipment.

Next to question ›