Before final inspection, the sprinkler contractor asks to monitor the fire pump. Which conditions are typically supervised at the fire alarm system for an electric fire pump?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1078
- A: Pump running, phase reversal, and loss of power or phase
Explanation
For an electric fire pump, NFPA 20 and NFPA 72 call for supervision of pump running, loss of power or phase, and phase reversal where the controller provides those outputs. Running is often treated as supervisory or alarm according to the approved design.
More questions: Installation
- 1079Which of the following is the best way to deal with a scope gap discovered mid-project, where the contract drawings show no detection in a new IT room that the code requires?
- 1080Why should a Level III verify the listing of every substituted device before it is installed?
- 1081During rough-in inspection on a new office building, you find several fire alarm junction boxes above a hard lid ceiling with no access panel. What is the main concern?
- 1082A fire alarm interface relay will release the hold-open power for corridor smoke doors. How should the release be wired so it is fail-safe?
- 1083On a project where the AHJ requires a fire watch during the cutover from the old system to the new one, who is normally responsible for providing it?
- 1084A technician sets the panel to bypass the entire third floor while the ceiling contractor works there. Which control does the Level III need to ensure?