Before final inspection, the sprinkler contractor asks to monitor the fire pump. Which conditions are typically supervised at the fire alarm system for an electric fire pump?

Exactly one answer is correct.

Show solution

Correct answer to question 1078

  • A: Pump running, phase reversal, and loss of power or phase

Explanation

For an electric fire pump, NFPA 20 and NFPA 72 call for supervision of pump running, loss of power or phase, and phase reversal where the controller provides those outputs. Running is often treated as supervisory or alarm according to the approved design.