How often must the functional test of system smoke detectors be performed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2005
- C: Annually
Explanation
The functional test, in which smoke or a listed aerosol is introduced so the detector alarms at the control unit, is an annual requirement. The separate sensitivity test follows its own schedule.
More questions: Maintenance
- 2006During annual testing, how should a restorable spot-type heat detector be tested?
- 2007A building has fixed-temperature, nonrestorable spot heat detectors that were installed 15 years ago. What does NFPA 72 require at this point?
- 2008How is a nonrestorable line-type heat detector checked during periodic testing?
- 2009How often must manual fire alarm boxes be functionally tested?
- 2010Which test frequency does NFPA 72 assign to mechanical (vane) and pressure-type waterflow alarm devices?
- 2011Under NFPA 25, how often must sprinkler control valve supervisory switches be tested?