Your service team has completed the first two required sensitivity tests on a building's smoke detectors and every detector was within its listed range both times. What may the ITM manager do?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2002
- C: Extend the sensitivity test interval, up to a maximum of 5 years
Explanation
After the second required calibration test, if the detectors remain within their listed sensitivity range, the interval may be extended, but not beyond 5 years. If a detector later falls outside its range, the testing frequency must return to the normal schedule.
More questions: Maintenance
- 2003Which method does NOT measure smoke detector sensitivity and therefore cannot be used to satisfy the sensitivity test requirement?
- 2004A sensitivity report shows 12 detectors outside their listed sensitivity range. What does NFPA 72 require for those detectors?
- 2005How often must the functional test of system smoke detectors be performed?
- 2006During annual testing, how should a restorable spot-type heat detector be tested?
- 2007A building has fixed-temperature, nonrestorable spot heat detectors that were installed 15 years ago. What does NFPA 72 require at this point?
- 2008How is a nonrestorable line-type heat detector checked during periodic testing?