Question 2003 of 297 · NICET Fire Alarm Systems Level III

Which method does NOT measure smoke detector sensitivity and therefore cannot be used to satisfy the sensitivity test requirement?

Exactly one answer is correct.

Show solution

Correct answer to question 2003

  • A: Spraying listed aerosol smoke into the detector to make it alarm

Explanation

A functional test with aerosol only proves the detector alarms, not where its sensitivity lies within the listed range. Acceptable sensitivity methods include calibrated test methods, the manufacturer's calibrated instrument, listed control equipment arranged to measure sensitivity, and other methods acceptable to the AHJ.