Which method does NOT measure smoke detector sensitivity and therefore cannot be used to satisfy the sensitivity test requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2003
- A: Spraying listed aerosol smoke into the detector to make it alarm
Explanation
A functional test with aerosol only proves the detector alarms, not where its sensitivity lies within the listed range. Acceptable sensitivity methods include calibrated test methods, the manufacturer's calibrated instrument, listed control equipment arranged to measure sensitivity, and other methods acceptable to the AHJ.