Question 2004 of 297 · NICET Fire Alarm Systems Level III
A sensitivity report shows 12 detectors outside their listed sensitivity range. What does NFPA 72 require for those detectors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2004
- B: Clean and recalibrate them, or replace them
Explanation
Detectors found outside their listed sensitivity range must be cleaned and recalibrated or replaced. A detector that is too sensitive causes nuisance alarms, and one that is not sensitive enough may respond too late.