A sensitivity report shows 12 detectors outside their listed sensitivity range. What does NFPA 72 require for those detectors?

Exactly one answer is correct.

Show solution

Correct answer to question 2004

  • B: Clean and recalibrate them, or replace them

Explanation

Detectors found outside their listed sensitivity range must be cleaned and recalibrated or replaced. A detector that is too sensitive causes nuisance alarms, and one that is not sensitive enough may respond too late.