Question 3041 of 297 · NICET Fire Alarm Systems Level III
Under NFPA 101, when is a fire alarm system required in a new business occupancy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3041
- B: 2+ stories above exit discharge, 50+ above or below it, or 300+ total
Explanation
NFPA 101 38.3.4 requires a fire alarm system in new business occupancies that are two or more stories above the level of exit discharge, have 50 or more occupants above or below it, or have a total occupant load of 300 or more.
More questions: Submittal Preparation and System Layout
- 3042Under the IBC and IMC, smoke detectors in return air ducts of an HVAC unit are generally required above which airflow?
- 3043A plans reviewer asks for proof that two-wire smoke detectors will work with your selected control unit. What should you submit?
- 3044A speaker circuit has 22 speakers tapped at 1 W and 8 speakers tapped at 2 W. The design rule leaves 20 percent spare amplifier capacity. What minimum amplifier rating is needed?
- 3045A 24 V power supply has a 6 A output. Strobes on four circuits draw 1.4 A, 1.6 A, 1.2 A, and 1.5 A in alarm. Is the supply adequate?
- 3046Why must strobe current values be taken at the lowest operating voltage when sizing circuits?
- 3047Where more than two visible appliances are in the field of view, what must the design provide?