Question 3042 of 297 · NICET Fire Alarm Systems Level III

Under the IBC and IMC, smoke detectors in return air ducts of an HVAC unit are generally required above which airflow?

Exactly one answer is correct.

Show solution

Correct answer to question 3042

  • C: 2,000 cfm

Explanation

The IMC requires duct smoke detectors in return air systems with a design capacity greater than 2,000 cfm, with exceptions, to shut down the unit on smoke detection. NFPA 90A has similar requirements.

Next to question ›