Question 1001 of 243 · NICET Fire Alarm Systems Level IV
A hospital addition ties a new fire alarm network node into the existing campus system, smoke control, elevator recall and door release. Which document governs the testing that proves these interconnected systems work together as intended?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1001
- C: NFPA 4, the standard for integrated fire protection and life safety system testing
Explanation
NFPA 4 covers integrated testing, meaning verification that separate systems such as fire alarm, smoke control, elevators and door hardware respond together as designed. NFPA 72 only proves the fire alarm side of each interface. NFPA 25 and NFPA 110 address their own systems, not the combined response.
More questions: Installation, Planning and Maintenance Management
- 1002On a commissioning project, which document is written by the design team to explain how the owner's project requirements will be met, including code basis, assumptions and system descriptions?
- 1003Under the commissioning process described in NFPA 3, who normally develops the owner's project requirements (OPR)?
- 1004Six addressable smoke detectors are added to an existing loop, and the program is edited to map them to an existing elevator recall output. What reacceptance testing is required?
- 1005After a change to site-specific software, NFPA 72 requires testing of all functions known to be affected by the change. What additional sample of initiating devices not directly affected must also be tested?
- 1006Under NFPA 72, who is responsible for the inspection, testing and maintenance of a fire alarm system and its interconnected emergency control functions?
- 1007You are setting up an ITM program for a 40 story office tower. How often must sensitivity of the spot-type smoke detectors be checked after the first year test, assuming each result stays within the listed range?