Question 1006 of 243 · NICET Fire Alarm Systems Level IV
Under NFPA 72, who is responsible for the inspection, testing and maintenance of a fire alarm system and its interconnected emergency control functions?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1006
- A: The property or building owner, or the owner's designated representative
Explanation
NFPA 72 places ITM responsibility on the owner or the owner's designated representative. The owner may delegate the work by contract, but the duty stays with the owner. The AHJ enforces, and the supervising station only receives signals.
More questions: Installation, Planning and Maintenance Management
- 1007You are setting up an ITM program for a 40 story office tower. How often must sensitivity of the spot-type smoke detectors be checked after the first year test, assuming each result stays within the listed range?
- 1008In the ITM schedule you are building, how often must waterflow alarm devices and valve supervisory switches be functionally tested?
- 1009A facility has nonrestorable fixed temperature spot heat detectors installed 15 years ago. What does NFPA 72 require for these detectors?
- 1010Before starting the annual test of a monitored system in a hotel, which step does NFPA 72 require regarding signal recipients?
- 1011A data center fire alarm system interfaces with a preaction releasing panel, HVAC shutdown and door unlocking. What must be in place before the periodic test begins?
- 1012Under the International Fire Code, a required fire alarm system is out of service. What must happen?