Question 1004 of 243 · NICET Fire Alarm Systems Level IV
Six addressable smoke detectors are added to an existing loop, and the program is edited to map them to an existing elevator recall output. What reacceptance testing is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1004
- A: Test the new detectors and every function they are programmed to control, including the recall output
Explanation
Reacceptance testing applies to added or changed devices and to the functions they operate. Because the new detectors drive elevator recall, that output must be proven too. A full building retest is not required for added devices, but skipping tests until the next annual visit is not allowed.
More questions: Installation, Planning and Maintenance Management
- 1005After a change to site-specific software, NFPA 72 requires testing of all functions known to be affected by the change. What additional sample of initiating devices not directly affected must also be tested?
- 1006Under NFPA 72, who is responsible for the inspection, testing and maintenance of a fire alarm system and its interconnected emergency control functions?
- 1007You are setting up an ITM program for a 40 story office tower. How often must sensitivity of the spot-type smoke detectors be checked after the first year test, assuming each result stays within the listed range?
- 1008In the ITM schedule you are building, how often must waterflow alarm devices and valve supervisory switches be functionally tested?
- 1009A facility has nonrestorable fixed temperature spot heat detectors installed 15 years ago. What does NFPA 72 require for these detectors?
- 1010Before starting the annual test of a monitored system in a hotel, which step does NFPA 72 require regarding signal recipients?