Six addressable smoke detectors are added to an existing loop, and the program is edited to map them to an existing elevator recall output. What reacceptance testing is required?

Exactly one answer is correct.

Show solution

Correct answer to question 1004

  • A: Test the new detectors and every function they are programmed to control, including the recall output

Explanation

Reacceptance testing applies to added or changed devices and to the functions they operate. Because the new detectors drive elevator recall, that output must be proven too. A full building retest is not required for added devices, but skipping tests until the next annual visit is not allowed.