Question 1007 of 243 · NICET Fire Alarm Systems Level IV
You are setting up an ITM program for a 40 story office tower. How often must sensitivity of the spot-type smoke detectors be checked after the first year test, assuming each result stays within the listed range?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1007
- C: Every alternate year, extendable to a maximum of 5 years after the second required test
Explanation
Smoke detector sensitivity is checked within 1 year after installation and then every alternate year. If the detectors stay within their listed range after the second required test, the interval may be lengthened to a maximum of 5 years. Detectors that drift outside the range must be cleaned, recalibrated or replaced.
More questions: Installation, Planning and Maintenance Management
- 1008In the ITM schedule you are building, how often must waterflow alarm devices and valve supervisory switches be functionally tested?
- 1009A facility has nonrestorable fixed temperature spot heat detectors installed 15 years ago. What does NFPA 72 require for these detectors?
- 1010Before starting the annual test of a monitored system in a hotel, which step does NFPA 72 require regarding signal recipients?
- 1011A data center fire alarm system interfaces with a preaction releasing panel, HVAC shutdown and door unlocking. What must be in place before the periodic test begins?
- 1012Under the International Fire Code, a required fire alarm system is out of service. What must happen?
- 1014A fire alarm contractor agrees to install a high-rise voice system for a fixed total price regardless of the actual cost. Which contract type is this, and who carries the risk of cost overruns?