Question 1005 of 243 · NICET Fire Alarm Systems Level IV

After a change to site-specific software, NFPA 72 requires testing of all functions known to be affected by the change. What additional sample of initiating devices not directly affected must also be tested?

Exactly one answer is correct.

Show solution

Correct answer to question 1005

  • A: 10 percent of them, up to a maximum of 50 devices

Explanation

When site-specific software is changed, the affected functions are tested 100 percent, plus a sample of 10 percent of the initiating devices that were not directly affected, capped at 50 devices. The sample guards against unintended side effects of the program change.

Next to question ›