Under the commissioning process described in NFPA 3, who normally develops the owner's project requirements (OPR)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1003
- C: The owner, with help from the commissioning authority if one is engaged
Explanation
The OPR captures what the owner needs from the systems, so it originates with the owner, often facilitated by the commissioning authority. Contractors and the AHJ respond to it rather than write it.
More questions: Installation, Planning and Maintenance Management
- 1004Six addressable smoke detectors are added to an existing loop, and the program is edited to map them to an existing elevator recall output. What reacceptance testing is required?
- 1005After a change to site-specific software, NFPA 72 requires testing of all functions known to be affected by the change. What additional sample of initiating devices not directly affected must also be tested?
- 1006Under NFPA 72, who is responsible for the inspection, testing and maintenance of a fire alarm system and its interconnected emergency control functions?
- 1007You are setting up an ITM program for a 40 story office tower. How often must sensitivity of the spot-type smoke detectors be checked after the first year test, assuming each result stays within the listed range?
- 1008In the ITM schedule you are building, how often must waterflow alarm devices and valve supervisory switches be functionally tested?
- 1009A facility has nonrestorable fixed temperature spot heat detectors installed 15 years ago. What does NFPA 72 require for these detectors?