A data center fire alarm system interfaces with a preaction releasing panel, HVAC shutdown and door unlocking. What must be in place before the periodic test begins?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1011
- A: A written test plan that defines the scope and how each interfaced function will be handled during testing
Explanation
NFPA 72 requires a written test plan that establishes the scope of the test, especially where emergency control functions and releasing systems could cause shutdowns or a discharge. The plan tells the team which outputs are tested live, which are bypassed and how they are restored.
More questions: Installation, Planning and Maintenance Management
- 1012Under the International Fire Code, a required fire alarm system is out of service. What must happen?
- 1014A fire alarm contractor agrees to install a high-rise voice system for a fixed total price regardless of the actual cost. Which contract type is this, and who carries the risk of cost overruns?
- 1015An owner wants to pay the contractor's actual costs plus a fee, but with a ceiling the price cannot exceed. Which contract arrangement fits?
- 1016A campus retrofit is priced at a fixed amount per installed device because the final device count is not known at bid time. Which contract type is this?
- 1017The general contractor withholds 10 percent of each progress payment from the fire alarm subcontractor until the project is accepted. What is this withheld money called?
- 1018A contract states that the contractor will owe the owner 1,500 dollars for each calendar day the fire alarm acceptance test is late. What is this provision called?