Question 1011 of 243 · NICET Fire Alarm Systems Level IV

A data center fire alarm system interfaces with a preaction releasing panel, HVAC shutdown and door unlocking. What must be in place before the periodic test begins?

Exactly one answer is correct.

Show solution

Correct answer to question 1011

  • A: A written test plan that defines the scope and how each interfaced function will be handled during testing

Explanation

NFPA 72 requires a written test plan that establishes the scope of the test, especially where emergency control functions and releasing systems could cause shutdowns or a discharge. The plan tells the team which outputs are tested live, which are bypassed and how they are restored.

Next to question ›