Question 1008 of 243 · NICET Fire Alarm Systems Level IV
In the ITM schedule you are building, how often must waterflow alarm devices and valve supervisory switches be functionally tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1008
- C: Semiannually
Explanation
Table 14.4.3.2 lists waterflow devices and valve supervisory switches for semiannual functional testing. Quarterly is a common NFPA 25 inspection interval for the devices themselves, which is a frequent mix up.
More questions: Installation, Planning and Maintenance Management
- 1009A facility has nonrestorable fixed temperature spot heat detectors installed 15 years ago. What does NFPA 72 require for these detectors?
- 1010Before starting the annual test of a monitored system in a hotel, which step does NFPA 72 require regarding signal recipients?
- 1011A data center fire alarm system interfaces with a preaction releasing panel, HVAC shutdown and door unlocking. What must be in place before the periodic test begins?
- 1012Under the International Fire Code, a required fire alarm system is out of service. What must happen?
- 1014A fire alarm contractor agrees to install a high-rise voice system for a fixed total price regardless of the actual cost. Which contract type is this, and who carries the risk of cost overruns?
- 1015An owner wants to pay the contractor's actual costs plus a fee, but with a ceiling the price cannot exceed. Which contract arrangement fits?