A facility has nonrestorable fixed temperature spot heat detectors installed 15 years ago. What does NFPA 72 require for these detectors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1009
- D: Replace them, or send 2 per 100 for laboratory testing and repeat that every 5 years
Explanation
Nonrestorable heat detectors cannot be field tested without destroying them. At 15 years they are replaced, or a sample of 2 per 100 is sent for laboratory testing, and the sampling is repeated at 5 year intervals. A failure in the sample triggers testing of more detectors.
More questions: Installation, Planning and Maintenance Management
- 1010Before starting the annual test of a monitored system in a hotel, which step does NFPA 72 require regarding signal recipients?
- 1011A data center fire alarm system interfaces with a preaction releasing panel, HVAC shutdown and door unlocking. What must be in place before the periodic test begins?
- 1012Under the International Fire Code, a required fire alarm system is out of service. What must happen?
- 1014A fire alarm contractor agrees to install a high-rise voice system for a fixed total price regardless of the actual cost. Which contract type is this, and who carries the risk of cost overruns?
- 1015An owner wants to pay the contractor's actual costs plus a fee, but with a ceiling the price cannot exceed. Which contract arrangement fits?
- 1016A campus retrofit is priced at a fixed amount per installed device because the final device count is not known at bid time. Which contract type is this?