When should spot-type smoke detectors normally be installed in a building under construction?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1035
- A: After construction cleanup, unless the AHJ requires them earlier for protection
Explanation
Construction dust can contaminate smoke detectors and cause nuisance alarms or loss of sensitivity. NFPA 72 has detectors installed after cleanup. Where detectors are needed earlier, they are protected and then cleaned or replaced and tested before acceptance.
More questions: Installation, Planning and Maintenance Management
- 1036A building owner asks whether an existing fire alarm system must be upgraded to the newly adopted NFPA 72 edition. Absent other requirements, what is the general rule?
- 1037A service sales manager is preparing an RFP response for the annual testing of a 300 building portfolio. Which item should drive the labor estimate most directly?
- 1038Your company is replacing an obsolete control unit but keeping the existing conventional 2-wire smoke detectors. What must be confirmed before the new unit is ordered?
- 1039When a fire alarm contractor's project manager plans a large project, why is a schedule of values submitted early in the job?
- 1040A project manager is told a key activity on the critical path will finish 5 days late. Which response directly protects the project completion date?
- 1041Which closeout item gives the owner the narrative description of the system, operator instructions and the procedures for routine maintenance and testing?