A building owner asks whether an existing fire alarm system must be upgraded to the newly adopted NFPA 72 edition. Absent other requirements, what is the general rule?

Exactly one answer is correct.

Show solution

Correct answer to question 1036

  • D: Existing systems need not be brought up to the new edition unless the code or the AHJ requires it

Explanation

NFPA 72 is generally not retroactive: installations that existed or were approved before the effective date need not be updated unless the code says otherwise or the AHJ determines that a condition presents an unacceptable risk. The 2025 edition reworded this clause for clarity without changing the intent.