Your company is replacing an obsolete control unit but keeping the existing conventional 2-wire smoke detectors. What must be confirmed before the new unit is ordered?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1038
- B: That the detectors are listed as compatible with the new control unit
Explanation
Two-wire smoke detectors draw power from the initiating device circuit, so they must be listed as compatible with the specific control unit. An incompatible combination can fail to alarm or fail to report a trouble. The compatibility list from the control unit manufacturer is the reference.
More questions: Installation, Planning and Maintenance Management
- 1039When a fire alarm contractor's project manager plans a large project, why is a schedule of values submitted early in the job?
- 1040A project manager is told a key activity on the critical path will finish 5 days late. Which response directly protects the project completion date?
- 1041Which closeout item gives the owner the narrative description of the system, operator instructions and the procedures for routine maintenance and testing?
- 1042A construction manager asks when the fire alarm contractor's warranty period normally starts. What is the most common contract answer?
- 1043At the acceptance test for a new voice evacuation system, the contractor should already have completed which step?
- 1044A cost report shows a job is 50 percent complete, with 62,000 dollars spent against a 110,000 dollar total cost budget. What is the projected cost at completion if the overrun rate continues?