Question 2062 of 172 · Texas Fire Alarm License Exam
A wire-to-wire short on a supervised notification appliance circuit normally causes
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2062
- A: a trouble signal
Explanation
NACs are supervised in reverse polarity through the EOL resistor, and a short is detected as a trouble so the panel will not drive current into the fault.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2063Polarized notification appliances on a supervised NAC allow the control unit to
- 2064A panel shows a ground fault trouble. A common first step to locate it is to
- 2065With an IDC disconnected from the panel, an ohmmeter across the loop reads infinite resistance. This indicates
- 2066Disconnected from the panel, a healthy Class B IDC with a 4.7 kilohm EOL resistor should read approximately
- 2067To measure the current drawn by a notification appliance circuit with a standard multimeter, the meter must be connected
- 2068Under Article 760, which cable type may be used as a substitute for type FPLR riser cable?