Polarized notification appliances on a supervised NAC allow the control unit to
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2063
- B: pass supervisory current only through the end-of-line device
Explanation
In standby the panel reverses polarity so that blocking diodes in the appliances stop current, and the supervision current flows through the EOL resistor only.