A panel shows a ground fault trouble. A common first step to locate it is to
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2064
- C: disconnect circuits one at a time until the trouble clears
Explanation
Isolating circuits one at a time narrows the fault to one circuit, which can then be split in halves until the grounded conductor or device is found.