With an IDC disconnected from the panel, an ohmmeter across the loop reads infinite resistance. This indicates
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2065
- D: an open in the circuit
Explanation
A healthy circuit reads close to the end-of-line resistor value. An infinite reading means the path to the EOL is broken, while near zero means a short.