To measure the current drawn by a notification appliance circuit with a standard multimeter, the meter must be connected
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2067
- B: in series with the circuit
Explanation
An ammeter must be placed in the path of the current, in series. Connecting it in parallel can create a short through the meter.
More questions: Texas Technician Technical Knowledge (NFPA 72-2019)
- 2068Under Article 760, which cable type may be used as a substitute for type FPLR riser cable?
- 2069Article 760 requires exposed fire alarm cables to be
- 2070The branch circuit supplying fire alarm equipment must NOT be
- 2071For NPLFA circuits, 18 AWG conductors must have overcurrent protection not exceeding
- 2072The minimum conductor size permitted for non-power-limited fire alarm circuits in a multiconductor cable is
- 2073When fire alarm cables pass through a fire-rated wall, the penetration must be