A new wall was built in an open office, splitting a room so one part has no smoke detector. Which inspection step should catch this?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2023
- C: The visual inspection
Explanation
Visual inspections include looking for building changes such as new walls, ceiling modifications, or occupancy changes that affect device placement. These are reported to the owner as deficiencies.
More questions: Maintenance
- 2025What test equipment is typically used for annual functional testing of spot smoke detectors in place?
- 2026What is the correct way to functionally test a restorable heat detector?
- 2027A technician bypasses a zone for testing and forgets to restore it. What risk does this create?
- 2028The control unit shows a ground fault trouble. What is the most efficient first step to locate it?
- 2029A technician measures resistance from one conductor of a disconnected circuit to a known building ground. Which reading suggests a ground fault?
- 2030With field wiring disconnected and the far end of a Class B IDC open (EOL removed), what reading between the two conductors indicates a short?